Working on a 7500sft house with an existing 200A 208V 3phase service. The Majority of the house is going to be gutted, so everything will be new.
The heating and cooling loads consist of the following:
A/C: 13KW chiller with 12 fan coil units
Heating: Gas Boiler with (6) 3.3KW (19.8kw total) humidifiers and the same 12fan coil units as the A/C.
Would the humidiers and fan coil units be considered an appliance? If so then clearly the A/C would be the larger of the loads and would be calculated at 100% where the humidiers and fan coil units can be diverisified with the appliances. But, if the humidiers and fan coil units are considered part of the heating load, then they would be more than the A/C at 19.8KW vs the 13KW.
The way I read the code, the fan coils units are considered an appliance (fastened in place) and do not produce the heat, like electrical baseboard would, but simply distribute the heat even though they are associated with the heating system. Same with the humidifiers except that they do not produce heat but are associated with the heating system. I was curious what everyones take was on this.
If the humidifiers and fan coil units are considered appliances then the 200A service can remain, but if not, the service would need to be upgraded. Thanks for everyones help.