P Part 77 Member Location WA state Oct 16, 2010 #1 No code book handy here at home tonight. Abandonded circuits shall be removed (or words to that effect). Which Article states that. TIA
No code book handy here at home tonight. Abandonded circuits shall be removed (or words to that effect). Which Article states that. TIA
J jusme123 Senior Member Location NY Occupation JW Oct 16, 2010 #2 645.2 I.T. Equipment 760.25 fire alarm - states that abandoned cables shall be removed both these articles deal with abandoned cables/circuits, what are you looking for? Last edited: Oct 16, 2010
645.2 I.T. Equipment 760.25 fire alarm - states that abandoned cables shall be removed both these articles deal with abandoned cables/circuits, what are you looking for?
Jim W in Tampa Senior Member Location Tampa Florida Oct 16, 2010 #4 Who says abanded ? I say they are for future equipment.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 16, 2010 #5 Most non chapter 3 wiring methods that are abandoned must be removed or tagged for future use.