3 Phase 4 Wire Supply
electrics
What does this mean? İt is in a nec book.
"in a single-phase panel fed by a 3-phase, 4-wire,
120/240-V delta supply where the loads served by the panel were predominantly single-phase,"
How can a supply like this feed a "single" phase panel ?
Can you reference what NEC book ?
It is somewhat common to have single phase sub-panels on a 3 phase supply, especially 3 phase 4 w 240/120 where the 3 phase load is often
limited.
McGraw-Hill?s
NATIONAL ELECTRICAL CODE? 2008 HANDBOOK page 894
İt is about delta breakers .But what does it mean? Does it mean you just use two wire (phase and neutral)I couldnt understand what is this delta breaker in fact...
Delta breakers are now obsolete and not allowed in new installations.
There was a time when 3 phase 4 wire 240/120 services were common for small commercial business with one or two three phase loads. Delta breakers were 3 phase breakers which could be installed in a single phase panel and they had a wire stubbed out for the line side of the third phase.
see 408.36(C)
The 120/240v section of a high-leg Delta 3-ph supply is exactly, and I mean exactly the same as a 120/240v 1-ph supply.
In fact, the high-leg Delta began as a 3-ph conversion to existing 1-ph services, simply by adding one more line conductor.
So we talk about a" 240 volt delta 3 phase" converted to "one with high leg " delta true?
so you dont use the other conductor of the 3 phase delta ? true? So why delta breaker is manufactured and why was banned ?
see 408.36(C)
Are you referring to delta rated breakers meaning a straight 240V vs. a 120/240V slash rated breaker?
No, in this case I am referring to "delta breakers" as referenced in 408.36(C). Three pole breakers with two "stabs" and one wire for line feed.
Like me, dinosaurs.
Whether there's a high leg depends on which conductor is grounded. If the center of one secondary is grounded, the opposing line is the high leg. That's what I described above.
Otherwise, either any line is grounded, creating a corner-grounded Delta; or no lines are grounded, and you have a floating Delta, which requires ground-detection.
Not for line-to-neutral loads, nor for line-to-line loads that require the neutral. Line-to-line loads that do not use the neutral can use any two lines, even the high leg.
Imagine an existing 120/240v 1-ph service like your home has, and you want to add a 3-ph motor. You have two lines, so the POCO must add one more, either one more transformer and supply an open Delta, or two and supply a full Delta.
The meter can would be swapped out for a 3-ph one, and the additional line added to the service entrance, and run directly to the "in" terminal on a Delta breaker, which has four bodies, like a 3-ph shunt-trip breaker.
The original two poles of the breaker receive power from the stabs as usual, and the third pole is fed via a terminal on the fourth body. The back of the breaker has two stab clips and two empty holes.
So, even though the existing service has only two lines, a 3-ph load could be supplied from the original panel. It probably became illegal because throwing the main did not deenergize the third phase.