I have self contained AC unit with a FLA of 85 amps. This unit is supplied from 100a three pole breaker in the cellar level two floors below the AC unit.
There was a 100a non fused switch installed within sight of the unit. This switch was removed and replaced with a VFD that has its own on/off switch.
The VFD now feeds the self contained AC unit, however the VFD is only supposed to control the fan and NOT the compressor. One idea is to tap the line side of the VFD with full size wire and feed a new switch that will be mounted on the unit and feed the compressor portion of the unit. We will rework the internals to seperate the feeds. My concern is that now there will be two service switches. The only simultanious disconnect will be from the 100a breaker located in the cellar. The VFD and new switch will be upto 10 feet away from eachother so I certainly would not consider them grouped.
Would this instlation be acceptable?
There was a 100a non fused switch installed within sight of the unit. This switch was removed and replaced with a VFD that has its own on/off switch.
The VFD now feeds the self contained AC unit, however the VFD is only supposed to control the fan and NOT the compressor. One idea is to tap the line side of the VFD with full size wire and feed a new switch that will be mounted on the unit and feed the compressor portion of the unit. We will rework the internals to seperate the feeds. My concern is that now there will be two service switches. The only simultanious disconnect will be from the 100a breaker located in the cellar. The VFD and new switch will be upto 10 feet away from eachother so I certainly would not consider them grouped.