MV Cable in Class 1 Div 2 Location

Status
Not open for further replies.

srsmith

New member
Can you use 4" liquid tight flex conduit for MV cable in a class 1 Div 2 location?
With a conduit seal on the motor terminal box and one above the concrete in
which it enters the classified area.
 
Can you use 4" liquid tight flex conduit for MV cable in a class 1 Div 2 location?
Yes. 501.10(B)(2)(3) or (4)

With a conduit seal on the motor terminal box and one above the concrete in which it enters the classified area.
Hmm... I was thinking you may be able to get by with one seal, then I thought the LFMC/LNMC would mandate two, but I can find no such requirement. Using one would be dependent on distance from enclosure to CID2-unclassified boundry being max of 11' 6" (18" enclosure to seal... 10' seal to boundry) as the conduit runs and also subject to the no-fitting requirement.
 
...Hmm... I was thinking you may be able to get by with one seal, then I thought the LFMC/LNMC would mandate two, but I can find no such requirement. Using one would be dependent on distance from enclosure to CID2-unclassified boundry being max of 11' 6" (18" enclosure to seal... 10' seal to boundry) as the conduit runs and also subject to the no-fitting requirement.
He only needs one seal at the boundary. There is no need for a seal at the motor terminal box since it isn't required to be explosionproof.
 