That is allowable.The main for the transformer now is three floors above the transformer.
450.14 Disconnecting Means. Transformers, other than
Class 2 or Class 3 transformers, shall have a disconnecting
means located either in sight of the transformer or in
a remote location. Where located in a remote location,
the disconnecting means shall be lockable, and the location
shall be field marked on the transformer.
This requirement will be modified in the 2011 NEC.
This is one of the changes in the '11 that I see costing some contractor a ton of money.
Not with a breaker locking means.This is one of the changes in the '11 that I see costing some contractor a ton of money.
....... and they blindly obey without looking it up, or asking for an article.I was describing the contractors who do not pay attention to the NEC and the inspector comes along and tells them they need a disconnect......