NEC rules for sizing cables and gensets

Status
Not open for further replies.
Please give extracts from NEC the guidelines for sizing cables and gensets for
a)different types of loads like intermittant(elevators),periodical,short-time etc
and for
b)different types of starting methods like across the line,wye-delta,auto transformer,vsd,vfd,shunt capacitor etc
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
A majority of the issues you are asking about are not regulatory, rather they are design issues. The NEC does not do very well at specifying design issues.

A good initial reference source is IEEE 446, Emergency and Standby Power Systems for Industrial and Commercial Applications (Orange Book).

ice
 

tom baker

First Chief Moderator
Staff member
Please give extracts from NEC the guidelines for sizing cables and gensets for
a)different types of loads like intermittant(elevators),periodical,short-time etc
and for
b)different types of starting methods like across the line,wye-delta,auto transformer,vsd,vfd,shunt capacitor etc

Thats far beyond the scope of a typical question we see. The NEC is prescriptive, IE follow the rules in Art 310 on condutor sizing. Your are asking performance type questions, thats not practible to answer here.
 
NFPA document

NFPA document

Can someone give the document number for the "maximum allowable voltage and frequency drop at generator and motor terminals" during starting a heavy or motor load
 