sub panel on stair case

Status
Not open for further replies.

jetlag

Senior Member
I have seen post before on sub panel on the side of a stair case , not on the landing. I cant remember what the verdict was on that. I am running out of options as to where to place the subpanel . I thought I had a location in the air handler closet but I dont have but 34" clear in the front .
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
I have seen post before on sub panel on the side of a stair case , not on the landing. I cant remember what the verdict was on that. I am running out of options as to where to place the subpanel . I thought I had a location in the air handler closet but I dont have but 34" clear in the front .

you need 36 inches in front. see 110.26
As to stairs i see nothing to prohit it but sure don't like it much
 

jetlag

Senior Member
thanks rcarrol

thanks rcarrol

'08 NEC 240.24(F) Not Located over Steps.
You need at least 36" in front.

I believe it was allowed at one time but was changed . I have another location in a hall but will they allow on the 30" wide for 4" of that to be in a cased opening ? In other words I have a 26" wall beside a cased opening with no door.
 

rcarroll

Senior Member
I believe it was allowed at one time but was changed . I have another location in a hall but will they allow on the 30" wide for 4" of that to be in a cased opening ? In other words I have a 26" wall beside a cased opening with no door.
Correct. It's new for the '08 code.
I would be ok with the hall location.:)
 