netaguy
- Providence, RI
I am trying to determine the primary current rating of three 300KVA single phase transformers wired for three phase four wire output as attached.
Would I be correct that "each" primary phase could draw 12 1/2 amps?
amps = va / phase to phase voltage X 1.73 = 12.56
or would I not use sq root 3 as primary windings are single phase?
Thanks for you help.
* Edit use 13.8kv for primary and 480/277V for secondary in photo and swap H taps with X taps. The wiring is typical.