Motor branchcircuit wire size
arnettda
I use 430.22a to determine conducor size. 125% of FLC of 28 amps. equals 35 amps. Can I use the 75deg C column from 310-16 to size my wire which is 35 amps? Or does it need to be at 30 amps from 240.4, which would require me to use #8 instead of #10. Thanks
240.4(D) references 240.4(G) which allows you to use 310.16 ampacities keeping 110.14 in mind. If your terminations allow 75?, then you may use that column for Art 430 applications.
(the #10 would be allowed)
If my wires are installed underground in conduit I believe I need to use the 75deg C column?
430.22(A) leeds to 430.6(A)(1) also look at the tables that start at 430.247.
Remember your FLA is 35 amps look at 310.16 table #10 75deg =35 amps if you use #10 you would be loading it at 100% remeber the 80% rule that i can not find right now:grin: so i would go with # 8:)
keep in mind what augie points out 110.14 (C) Temperture Limitations
The load is actually 27 amps not 35 amps so with #10 conductor's he's really at 80%.