As an Elevator Inspector I have come across a common practice having the shunt trip breaker installed in the machine room and it being utilized as the elevator disconnect. NEC 620.51(B) requires the "power supply" to be opened prior to application of water. And based on the single line drawing figure 620.13 it can be presumed that the power supply originates from a MDP outside an elevator machine room. It is my concern that with the shunt breaker inside the room there is still a shock hazzard present in the room on the line side, which could electrically charge the conduit etc... additionally the code doesn't indicate a NEMA-4 enclosure requirement. And after all the disconnect in the room is only a means of opening the "power supply" and not the source of power.  Your thoughts please. Thanks Jim