need to derate conductors because there are approx 30 current carrying conductors in a conduit, wiring is for workstations. when is it applicable to use Table B.310.11 in Annex B?
I believe the table in annex b is the same one in 310.15(b)(2)(a)
The annex is just for informational purposes only.
You use that table anytime you have more than that 3 CCC's in a raceway. Also when bored holes are fire caulked and I think when cables are bundled together.
For 4-6 or 7-9 conductor the derating factors are the same as 310.15(b)(2)(a). When you exceed 9 CCC's you can use this table where the load diversity is 50%.
I'm guessing that this table will not apply to your installation.
For 4-6 or 7-9 conductor the derating factors are the same as 310.15(b)(2)(a). When you exceed 9 CCC's you can use this table where the load diversity factor is 50%.
Infinity will you define "load diversity factor" for me?
Derating and fill are two separate issues.
Derating is reducing the ampacity due to a variety of issues. Fill is how many little circles will fit inside a big circle.
You could simply use the NEC's definition. But then again, it doesn't have one. :roll:
By the way, the term is "load diversity," not "load diversity factor." ;)
Yes, the correct term is load diversity not load diversity factor.
I will correct my earlier post. :)
Here's a definition from IEEE:
The difference between the sum of the maxima
of two or more individual loads and the coincident of combined maximum load usually measured over a specified period.
Here's a simpler version:
Diversity occurs in an operating system because not all loads connected are operating simultaneously or are not simultaneously operating at their maximum rating.
I looked in the NEC and didn't see it anywhere so I thought I would ask. The wording is a little confusing. At least to me it is.:D