For 4-6 or 7-9 conductor the derating factors are the same as 310.15(b)(2)(a). When you exceed 9 CCC's you can use this table where the load diversity factor is 50%.
I'm guessing that this table will not apply to your installation.
You could simply use the NEC's definition. But then again, it doesn't have one. :roll:Infinity will you define "load diversity factor" for me?
By the way, the term is "load diversity," not "load diversity factor."![]()
The difference between the sum of the maxima
of two or more individual loads and the coincident of combined maximum load usually measured over a specified period.
Diversity occurs in an operating system because not all loads connected are operating simultaneously or are not simultaneously operating at their maximum rating.