Have a 30hp motor 208v 3ph with fla of 90amps. Engineer has 3-#1 and 1-#6 ground with a 100amp breaker. Is this correct??
Although I would probably have specified a larger breaker to avoid tripping from in-rush current.
and I think the minimum size for a breaker feeding a single motor is 125% of the motor rated current. That would mean a 125A breaker minimum.
I don't believe that there is any minimum required breaker size for a single motor based on the motor flc. However, the motor OCPD must be capable of carrying the starting current of the motor. If the 100A c/b can carry the starting current, then it is compliant.
That being said, it would be rare that you would want to protect conductors at a lower OCPD rating than the conductor ampacity because of the previously stated in-rush issue.