mustang1

New member
Have a 30hp motor 208v 3ph with fla of 90amps. Engineer has 3-#1 and 1-#6 ground with a 100amp breaker. Is this correct??
 
Have a 30hp motor 208v 3ph with fla of 90amps. Engineer has 3-#1 and 1-#6 ground with a 100amp breaker. Is this correct??

There's nothing wrong with it, it's code compliant; the conductors may have been upsized for voltage drop. Although I would probably have specified a larger breaker to avoid tripping from in-rush current.
 
Although I would probably have specified a larger breaker to avoid tripping from in-rush current.

Yes, I agree, and I think the minimum size for a breaker feeding a single motor is 125% of the motor rated current. That would mean a 125A breaker minimum.

On top of that, Elevator manufacturers usually point to the NEC 430.52 exceptions, and encourage using the largest circuit breaker size allowed. I assume this is because the motor can be expected to do a lot of starting, and also because you don't want to trap people in the elevator due to an undersized circuit breaker.
 
and I think the minimum size for a breaker feeding a single motor is 125% of the motor rated current. That would mean a 125A breaker minimum.

I don't believe that there is any minimum required breaker size for a single motor based on the motor flc. However, the motor OCPD must be capable of carrying the starting current of the motor. If the 100A c/b can carry the starting current, then it is compliant.
 
I don't believe that there is any minimum required breaker size for a single motor based on the motor flc. However, the motor OCPD must be capable of carrying the starting current of the motor. If the 100A c/b can carry the starting current, then it is compliant.

Correct; the 125% rule is for the conductor ampacity for continuous duty motors, not the OCPD. Also, an elevator is not considered a contiunous duty motor per Article 620.

That being said, it would be rare that you would want to protect conductors at a lower OCPD rating than the conductor ampacity because of the previously stated in-rush issue.
 
I don't believe that there is any minimum required breaker size for a single motor based on the motor flc. However, the motor OCPD must be capable of carrying the starting current of the motor. If the 100A c/b can carry the starting current, then it is compliant.

I'm so used to using 125% on motors, I'm not really sure if its a code requirement, or just standard practice.

But it looks to me that 220.18 would apply, since the branch circuit rating would be equal to the circuit breaker rating.

Steve
 
That being said, it would be rare that you would want to protect conductors at a lower OCPD rating than the conductor ampacity because of the previously stated in-rush issue.

I don't see that the conductor ampacity has anything to do with the OCPD rating. For instance, if you used a 110A c/b with #2 wire for this motor, and the 110A c/b carried the starting current; if you increased the wire size to 1/0 for voltage drop, would you increase the c/b to 150A or leave it at 110A?
 
Elevator cut sheets I see have the OCP size listed.

100A is way too small. Typical 30HP motor would use 175A OCB.

To confuse maters, most elevators I see use soft start.

RC
 