This is obviously an attempt at making the residential code on par with ADA standards although it is not quite there-  ADA , I believe, is 15 inches off the floor to bottom of the receptacle.
The one thing I noticed is that this rule appears to not allow a floor receptacle in the middle of the room for a lamp, etc. by a couch. That would not be a required outlet as it states in the OP's statement. This is wrong, IMO- even the ADA rule has a total exception for floor receptacles.
	
		
			
		
		
	
				