This my first post, but I appreciate all that others have contributed. The home I was inspecting today has two service panels. The Challenger panel data plates say they are 150 amps maximum. The wiring to the panels is 4/0 aluminum. Seeing the larger wire size, I didn't think anything of it until I came to the main disconnects at the exterior of the home. The disconnects are 200 amps. Any help with this would be greatly appreciated as I haven't come across mismatched disconnects before.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
No main breakers at the panels. The 200 amp main breakers are at the meter.
I suspect someone screwed up if the panels are in fact 150 amp buss bars. Simple fix is to change the breakers outside to 150 as long as the load will warrant that, otherwise get some 200 amp panels. Unfortunately this would not help the situation unless the feeder is in conduit.
 
I suspect someone screwed up if the panels are in fact 150 amp buss bars. Simple fix is to change the breakers outside to 150 as long as the load will warrant that, otherwise get some 200 amp panels. Unfortunately this would not help the situation unless the feeder is in conduit.

The home was built in 1997. The load is split between the two panels and I would suspect that installing 150 amp mains would pose not problems.
 

ceb58

Senior Member
Location
Raeford, NC
The home was built in 1997. The load is split between the two panels and I would suspect that installing 150 amp mains would pose not problems.

In 1997 4/0 al SER would have been good for 200amp but someone screwed up with the 150's. Simplest fix is to change the mains to 150amp. Under 08 code 4/0 SER is good up to 150amp.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Too bad. Although it's a poor choice, 10' or less and the 10' tap rule might apply.

You would still need 150 overcurrent protection for the panel.

I'm surprised that this house has Challenger equipment if it was built in 97. These panels must have been sitting in someones stock for at lease several years.
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
In 1997 4/0 al SER would have been good for 200amp but someone screwed up with the 150's. Simplest fix is to change the mains to 150amp. Under 08 code 4/0 SER is good up to 150amp.

We're still on 2005 here in VA, so I haven't bought the 2008 yet. Did they change the 315.15(b)(6) table in 2008?

Thanks,

Mark
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
No, they changed 338.10(B)(4). They deleted the exception to 334.80.

I guess I'm still missing something. The OP said it was a home, so why wouldn't you be able to use 310.15(b)(6)? How does that rule change under 2008?

Thanks,

Mark
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
My best guess is this was accidently over looked by either installer , inspector or both.
150 amp breaker would been same price but maybe not in stock. You have a violation but very unlikely would ever cause a problem unless its loaded with some very large loads that might be on at same time. Easy to fix but not cheap.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
This could turn into an interesting situation. Could the EC that installed this be forced to correct it being he created the violation. Warranty is one year but this is not really a warranty issue. If he sold this to be 400 amp service then what ?
Must say as a HI you were very alert.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm assuming that these panels are lighting and appliance panels so they would require overcurrent protection at or less than their rating.

You're correct. I was thinking of a different application. In the 2008 NEC the lighting and appliance panelboard reference has been removed. The new applicable section would be 408.36.
 