Wiring2010
Hi all,
I am turning down a rewire job to a Chinese restaurant because I do not like what I see on the existing panel. The connected loads are over the main which is a 200 amp breaker. There are two subpanels off the main panel. One subpanel is feed off a 30 amp two pole and the second subpanel is feed off a two pole 60 amp breaker. The owner doesn?t know what is on either subpanel. The owner wants to add additional ceiling lights but I am concerned that the main may pop. I cannot clamp the panel as this store had a fire a few months back (grease fire) and is under construction. I can only estimate by looking at what the ledger has for loads and figure from there.
Some facts; everything that is there now has worked in the past but now they want to add some huge ceiling fixtures plus additional cans ( 4 inch ) which is going to add to the load.
My question is how would you handle this? Would you count the number of circuit breakers and use that as a figure times a percentage? Thinking that not all the loads will be on at the same time. I was thinking of increasing the service but that would be costly but then I know I would have enough capacity for what is there.
So how would you handle the unknown meaning that that running current for the panel is not known but the connected load is and this connected load is more than the main.