hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
One of my techs has a store that reported a 200 amp breaker that was tripping taking down the lighting and computers and registers. He could not find anything wrong, so assumed iy must be a weak breaker (load was only 59 amps,) so he replaced it. They called back again saying the breaker was still tripping about every two hours. He baby sat it for four hours, and nothing happened. As soon as he went out to his truck to do the paperwork, it "tripped". Still could not find anything wrong. This "continued" for another day, and still nothing could be found. I drove 4 1/2 hours early Sunday morning to see what I could find out what the problem was. The store had turned off the breaker in fear of a fire overnight, so I cut it back on, and put a recorder on it. I never left it alone all day, when I was not there, my tech was. No problem all day. Left the recorder on overnight, no problems recorded. Let my tech go home the night before, so I was now the only one watching it. Worked fine for about three hours, but I had to step out for a conference call. After about 10 minutes, the manager came running out saying the registers were down! Went back in, the lights were still on (I locked that panel before I went out) but the breaker for the computer panel was TURNED off, not tripped. Whoever turned it off found out too late they could not turn off the lighting panel! (two totally seperate feeds from the service) Busted! They are going to put up a camera to try and catch which employee was doing this.