Article 409, the "SCCR" issue, applies to "Industrial Control Panels" as far as I can tell. But what is being considered an Industrial Control Panel? I have someone building a computer server rack. They are feeding it with 3 phase 4 wire, 480/277 then using the single phase 277V power off of that for the individual power supplies. They have 50kAIC available at the line terminals and are using a 65kAIC 3 phase main CB feeding a system of the UL1077 1 pole "supplementary protectors" rated 10kAIC to distribute that 1 phase power to the PSUs. I said the UL1077 units are insufficient and even if they used UL489 versions, if they are rated 10kAIC, it still won't pass muster by pointing to Article 409. I'm being told it doesn't apply because "this isn't an industrial control panel".
Thoughts?
Thoughts?