assuming the insulation of the cable is the same, can they be run in the same raceway ?
As long as one is not service conductors.assuming the insulation of the cable is the same, can they be run in the same raceway ?
Article pleaseAs long as one is not service conductors.
Article 230.Article please![]()
No, one isn't. The other one is.As long as one is not service conductors.
So if the secondary conductors are service conductors, what are the primary conductors?No, one isn't. The other one is.![]()
Article please![]()
So if the secondary conductors are service conductors, what are the primary conductors?
![]()
Thanks :d:d:d:d:d:d The smiles didn't appear........article 230.
I'll assume you want section, too...:d
230.7
Thanks :d:d:d:d:d:d The smiles didn't appear........
So if the secondary conductors are service conductors, what are the primary conductors?
Hmmm...since this is an NEC forum, we can only consider those conductors which fall under NEC purview. As such, if the secondary conductors are service conductors, the primary conductors may be service conductors, but they can only be POCO service conductors......
The primary side could be service conductor if you're stepping up the voltage before feeding a panel....no?