Oversized wire?
tonype
New Jersey
20-amp Square D breaker. Circuit wire is a #6 Al. Strands from the wire were separated and connected to the breaker, in a manner similar to double-lugging (each side of the screw). Is this proper?
Take a look at the circuit breaker lug and see if it rated for that size wire.
If it is then the wire should fit without the double twists
Nope. Since you said both sides of the screw I'm assuming that you mean a QO breaker. If I remember correctly they're typically good for up to a #8 conductor. As Leo stated the listing of the CB lug would provide the correct answer. This can be a simple fix by splicing on a smaller conductor.
Rob: You are correct - it is a QO breaker
Why not simply post the pic?