Article 314 and Wireways

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Good luck....
Based on previous threads, I'm afraid you will get opinions...it seems unavoidable from the wording:
(B) Metallic Wireways Used as Pull Boxes. Where insulated conductors 4 AWG or larger are pulled through a wireway, the distance between raceway and cable entries enclosing the same conductor shall not be less than that required by 314.28(A)(1) for straight pulls and 314.28(A)(2) for angle pulls.
I have seen a history of ROP and ROC comments which appear to only confuse the "intent".
As worded, I don't think there is little argument that 314.28 applies to
Art 376 in terms of distance between raceway entries...
if it goes further (raceway to opposite wall) becomes a debate.

The wording vs intent issue was discussed at length here:
http://forums.mikeholt.com/showthread.php?t=112571&highlight=376.23&page=4
 
Last edited:

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Is there a specific part of 314 or 376 you are looking at. Kind of a vague question.
 