I have a situation where we have panel A (3phase 4w) feeding panel B (3ph 3w), and panel B feeding another panel C (3ph 4w). Neutral for Panel C was connected to panel A neutral Bus, and routed from A via Panel B feeder conduit, then routed via Panel C feeder conduit to panel C. Does this installation violate NEC 200.3?
I tried to explain to inspector that this should be safe, since if someone turns off panel B feeder breaker (that is located in panel A), then the neutral in Panel A will be dead for Panel C. But the inspector is red tagging it since it voilate 200.3? Please advise.
My understanding of 200.3 is that it applies to utility supply, and that it is required that we have a neutral from utility that is solidly grounded.
Is there anywhere in the code that permit this installation?
I tried to explain to inspector that this should be safe, since if someone turns off panel B feeder breaker (that is located in panel A), then the neutral in Panel A will be dead for Panel C. But the inspector is red tagging it since it voilate 200.3? Please advise.
My understanding of 200.3 is that it applies to utility supply, and that it is required that we have a neutral from utility that is solidly grounded.
Is there anywhere in the code that permit this installation?