billsnuff
- East of 480sparky
No, a 1/2" metal water pipe with 10' in contact with the earth is still a grounding electrode per the definition given in 250.52(A)(1).Of course the NEC applies. You misinterpretted my post. If it's smaller than 3/4" then refer to 250.104 for bonding because it's not qualified as an electrode per 250.52(A)5.
Today isn't Talk Like a Pirate Day, is it?AAAAAAAAAAAARRRRRRRRRRRRRRRRRRRGGGGGGGGGGGGGGGGGGGHHHHHHHHHHHHHHH!................................................................................![]()
http://www.dca.ga.gov/development/constructioncodes/programs/codeAmendments.asp
I found this. Hope this is what you are looking for...
The technique is called FOP, or fall of potential.
Here is a link
http://www.megger.com/us/story/Index.php?ID=146
K8MHZ,
Try this for an interesting article on Grounding.
http://www.megger.com/common/documents/GroundTestingKey_AG_en.pdf
I've got to run but, reading the first few paragraphs I must point out that the author has a number of errors in his statements.
Roger
I think I see where the problem lies, the lesser the resistance, the higher the current would be.
Roger
Is it the poco or the ahj that makes you run #4?