Gentlemen,
I was hoping for a little proofreading from y'all...
I have a 125A subpanel to be installed in a workshop
125' from a single family dwelling. I will run PVC and 4 wires
out to the shop. I would like to keep Voltage drop to
a minimum knowing that I will be installing a welding outlet.
#1/0 copper, table 8 value of .122 ohm/kFT and table 9 value 0.12ohm/kFT
so AC and DC resistance are nearly the same, with 12.9 being the constant for copper
(2x12.9x125Ax125')/105600=3.82volts/240=1.6%
I can't know for sure just yet what the neutral load will be, so should I run a full sized
grounded conductor, can I only downsize if I know the load?
Would it be more practical/economical to use Aluminum conductors, in your opinion?
I'm another one of those guys who is only accustomed to spending other peoples'
money on commercial jobs....
Another question would be the disconnecting means, a 125A main breaker panel should
cover this right?
Thanks,
Charles
I was hoping for a little proofreading from y'all...
I have a 125A subpanel to be installed in a workshop
125' from a single family dwelling. I will run PVC and 4 wires
out to the shop. I would like to keep Voltage drop to
a minimum knowing that I will be installing a welding outlet.
#1/0 copper, table 8 value of .122 ohm/kFT and table 9 value 0.12ohm/kFT
so AC and DC resistance are nearly the same, with 12.9 being the constant for copper
(2x12.9x125Ax125')/105600=3.82volts/240=1.6%
I can't know for sure just yet what the neutral load will be, so should I run a full sized
grounded conductor, can I only downsize if I know the load?
Would it be more practical/economical to use Aluminum conductors, in your opinion?
I'm another one of those guys who is only accustomed to spending other peoples'
money on commercial jobs....
Another question would be the disconnecting means, a 125A main breaker panel should
cover this right?
Thanks,
Charles