Howdy,
Our data management folks are considering installing a busway system beneath the raised floor of their large computer room. This raised floor is 3 foot in height and the room was built to Art 645 requirements. I have a concern about clearances on the overcurrent devices that will be mounted to the busway. I have not seen detailed information on the system but believe it will consist of 225 amp bus with modular circuit breaker/receptacle units installed where required. Seems to me I should have 3 foor clear in front on any O.C. device installed to meet 110.26 (A) as I believe there will be times when "examination, adjustment, or maintenance while energized" might occur. Actually unless the entire busway is shut off, it almost always will occur. Could we satisfy the code if the devices were mounted so they face up? Then when we remove a floor tile we'll have clearance. Of course a bigger question might be: Can the busway be installed at all? I don't see it listed in 645.5 (D) but that seems to be dealing with the branch circuit wiring beneath a raised floor. I see nothing in 368 that would prevent installation of the busway below a raised floor.
Thanks for your time,
Jim
Jim