The potential exists for almost everything that comes with a 15a plug.How can the manufacture use a receptacle which is designed for a max 15 amps and draw 20amps?
110.3 b is pretty funny.
Thank you all for your responses. Although, I still don't see why this is allowed to be done. If manufactures can install 15amp plugs and draw 20 amps through them why have a 20 amp plug design?
Because of the welders duty cycle,
a welder with a 20% duty cycle can only weld for 20% of each hour which means the conductors will not be overheated.
A welders duty cycle is based on 10 minutes.
So if it is 20% duty cycle then a 2 minute weld on max setting is the longest weld you can make. Then the machine must rest for 8 minutes. You can weld longer if the amperage setting is turned down for thiner metals.