We have a customer with a 3000A service installed by us a few years ago. They have a 500HP compressor on a softstart fed from this gear that's been blowing fuses randomly. So one day when we're in the electrical room we noticed it made a terrible vibrating-rattle like noise on startup. Scary sounding enough, that my apprentice was halfway out the door when I looked around for him.....chicken!
Had the POCO shut them down today to check all the connections. All buss connections looked great, no heat marks anywhere, but we found six 3/8 x 1" bolts LOOSE where the bussing bolts to a long fiberglass insulator. The nuts on some of them were backed off about 2 turns and they were right over the Pringle main disconnect switch. I don't even want to think what would happen if one dropped...
But, a little loctite and now they're good to go!
Unfortunately, we turned the power back on and that damn vibrating/rattle is still there.
I really thought we had it. Now I'm thinking it's the sheetmetal at the back of the switchgear that I can't get to, that's causing the noise. Except for pulling the gear out to get to the back, I think the customer is going to have to live with it.