Is there any article in the NEC that requires a certain percentage of spares for a new panel installation?
Nothing specifically, as far as I know.
On rare occasions I have heard of AHJ's requiring such, possibly based on 90.8
I've had a couple jobs that required 25% spare breakers.
I agree with Gus. I have had AHJ's use 90.8 to require spare room in panelboards.
Does the AHJ change the rules for new panels vs additions to exisiting? If not these required spares can never be used.On rare occasions I have heard of AHJ's requiring such, possibly based on 90.8
I don't see how they can 'legally' do that.
What if the inspector decided I need to have an extra 50 amps available on a 100 amp service?
I have also seem many specs that require a 10% future space requirement for panelboards.
Chris
I too would question the "legality" of such a call, but, as has been mentioned here, sometimes it's easier to comply than "fight".
Memory does not allow to to be specific. My intent was simply to warn the OP that there are those who feel the answer to his question is "Yes"
Was that an engineering requirement or AHJ? If it's the engineer, hey I want a panel with 50% capacity and I'm willing to pay for it. If it's AHJ there's really no code to enforce that.
What is widely misunderstood is that Article 90 is only the introduction to the code which is comprised of 9 chapters and article 90 is in none of those 9 chapters, IOW's article 90 is not part of the actual code rules and is no more than a glorified FPN.If I put a 200AMP service in when only a 100AMP was required would that meet 90.8? No vacant space for additional breakers.
IMHO that is impossible to enforce. 90.8 does not meet 90.5(A).
Roger
Roger
Help me. I thought IF you wanted to enforce article 90 it had to be seperately codified. Is that correct?
Roger
What makes you believe article 90 is not part of the code? The introduction in 90.3 states what belongs and what doesn't. And it states the code is comprised of the introduction and nine chapters not just nine chapters. I guess I have to disagree that 90 is not code.
And I agree Bob, but I will explain my post a little betterRead the second sentence, it makes no mention of Chapter '0'.