As long as the cable is protected with a 100-a fuse or breaker, it's perfectly fine.
Hello and welcome.I have a bid from a contractor. They are replacing a 60amp fuse box and replacing it with a 125 amp subpanel and connecting it to the main panel in a seperate area. They want to use only 100 amp cable though. This doesn't sound right. I need opinions
My supply house only stocks 125A and up panels...
Hello and welcome.
If you are an Electrical contractor why are you getting bids for work you should be doing.
Are you really an electrical contractor?
As long as the cable is protected with a 100-a fuse or breaker, it's perfectly fine.
There is nothing in the NEC that I know about however many panels esp. 200 amp panels will not allow a breaker larger than 125 amps by the manufacture spec.Isnt there something in the code about a plug in breaker can not be over 100 amp ? Thats why people like feed the sub panels with 100 amp . I had a 125 plug in square D one time but I believe it went over the buss lugs on the left and right to cover 4 lugs.
What do you do if you only need like a little 70 amp 2 or 4 slot, go to HD?
I should of said they only stock 125A in 6 space and up panels.
I have a bid from a contractor. They are replacing a 60amp fuse box and replacing it with a 125 amp subpanel and connecting it to the main panel in a seperate area. They want to use only 100 amp cable though. This doesn't sound right. I need opinions
Hello and welcome.
If you are an Electrical contractor why are you getting bids for work you should be doing.
Are you really an electrical contractor?
He said he's a Contractor. He didn't say he was an Electrical Contractor. I think the mods would allow it...