conductor and fuse sizing

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This sounds like a study question so I'll point you in the right direction, read 240.4(D) and go on to the other sections mentioned for the whole picture.

Roger
 

jumper

Senior Member
We do not answer homework questions, but we are willing to help.

Post your answer as to why this may or may not be allowed and members are willing to help.

What do you make of Roger's response and why? It is a good starting point that he gave you.
 

JES2727

Senior Member
Location
NJ
Not necessarily, it could be acceptable for motor applications.

Chris

Yes, I'm well aware of the applications where a 30A breaker can be used with #12. But he's not asking about that. He's asking about the applications where you can not use a 30A breaker with #12. Sometimes it's not allowed.
It was an intentionally vague answer to a vague question.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
He's asking about the applications where you can not use a 30A breaker with #12.
No he's not, he's asking foa a "reason" not to use a 30 amp OCPD on a # 12 and your vague answer left alot to be desired. The question was not really vague but it is obviously a study question given the fact that the OP is a student.

Roger
 

JES2727

Senior Member
Location
NJ
OK, never mind. Some guys can crack wise on here and everybody laughs. And some guys can't.
Going back to lurking....
 

norcal

Senior Member
Hooked up a 4 ton A/C (only) that would have been acceptable for 14 AWG on a 30A, was not a bid job so used 10 AWG. (208V 3? 18.7A w/ a max OCPD of 30A). It took a long time for the rules for A/C equipment to sink in, now get a chuckle when home inspectors go ape (bleep) when they see 10 AWG w/ a 40A breaker on a A/C feed.
 