help sizing a junction box
jwjrw
I need to size a JB for #1 conductors (3 rhw/3 thwn). The JB will have (2) 1 1/4" emt conduits in it. One in the bottom. One out the back. Can someone walk me through sizing the box correctly? I seem to be confusing myself once again.:confused:
See if this helps. Wire size does not matter it is all about the conduit size.
ry%3D400
I think it confused me more.:grin:
Ok the "b" dimension must be 6 times 1 1/4" = 7.5 "
The "a" dimension shows 3 inches in table 312.6(a)
So is that a box 7.5" sq and 3 " deep?
7.5 " is correct but the width can be less so you can have a 4x8 that is 4" deep. More common would be 8x8x4 but it does not need to be any wider than to accommodate the conduit.
Thanks Dennis. It's been a while since I had to size a JB with conduit penetrations.
I thought the dimension "B" 1 1/4" cond. multiply by 6 for angle pull = 7.5" supposed to be minimum distance for closest section of conduit entry to the other conduit entry. So the box height should be more than 7.5".
7.5"+1 1/4"+1"=9.75" or say 10"
I would use at least 12" hieght box.
Here is what it states
Exception: Where a raceway or cable entry is in the wall of a box or conduit body opposite a removable cover, the distance from that wall to the cover shall be permitted to comply with the distance required for one wire per terminal in Table 312.6(A).
The distance between raceway entries enclosing the same conductor shall not be less than six times the metric designator (trade size) of the larger raceway.