1. SDS gen set located 50' from seperate structure with utility service at the seperate structure.
2. Gen is 480/277 with gen neutral bonded at gen set. There is a service rated disconnect at the generator.
3. There are no L-N loads and therefore the conduit from the genset to the ATS has 3 ungrounded cond and one EGC cond. The ATS has no neutral switch.
4. Both the generator and the seperate structure have grounding electrode systems at there respective locations.
Question: Can the two grounding electrode systems be bonded together with a conductor running in the same trench as the generator conduit?