When doing a load calculation, say for a 120/240 single dwelling home. Do you figure out the amps for all the 120v loads seperately from the 240v loads. Or do you find the total wattage and divide it all by 240 to figure out the service size? thank you
If this link does not work
http://www.mikeholt.com/documents/calculations/formulas/ResidentialLoadCalculations.xls
go here
http://www.mikeholt.com/freestuff.php?id=freegeneral
look for the res. load cal.
Remember that generally speaking all the 120v loads ill be somewhat equally divided between the phases thus you would use the 240V for your calculation.When doing a load calculation, say for a 120/240 single dwelling home. Do you figure out the amps for all the 120v loads seperately from the 240v loads. Or do you find the total wattage and divide it all by 240 to figure out the service size? thank you
OP is an apprentice, I believe OP is trying to learn in hopes of passing the test one day.
If I understand you, he should do it the old fashion way with a pencil and paper. I agree.
That is why when you hand the clerk $21.00 for $15.76 due they try to hand back the one dollar bill.
Total wattage/VA divided by 240. Annex D has some good examples
Can everyone get that link to work from the free stuff page? When I try to load it, it says cannot open because was not decoded?