392.7 Grounding.
(A) Metallic Cable Trays. Metallic cable trays that support
electrical conductors shall be grounded as required for
conductor enclosures in accordance with 250.96 and Part
IV of Article 250.
250.96 Bonding Other Enclosures.
(A) General. Metal raceways, cable trays, cable armor,
cable sheath, enclosures, frames, fittings, and other metal
non?current-carrying parts that are to serve as grounding
conductors, with or without the use of supplementary
equipment grounding conductors, shall be bonded where
necessary to ensure electrical continuity and the capacity to
conduct safely any fault current likely to be imposed on
them. Any nonconductive paint, enamel, or similar coating
shall be removed at threads, contact points, and contact
surfaces or be connected by means of fittings designed so
as to make such removal unnecessary.
250.86 Other Conductor Enclosures and Raceways. Except
as permitted by 250.112(I), metal enclosures and raceways
for other than service conductors shall be connected
to the equipment grounding conductor.