ELA
- Electrical Test Engineer
Bob in all honesty it has been about a year since I last visited LED's, so I am open to the idea they have improved considerably.
Now with that said the manufactures play a lot of game with LED's rating especially efficiency. They flat out misinform.
One when they state the lumens/w they do not include the driver power consumption. LED's are current devices. If the driver is a shunt linear regulator current in = current out. So if the source is DC say 12 VDC and the LED is rated .35 amps at 3 volts for a 1 watt lamp, the driver uses (12 volts - 9 volts) x .35 amps = 3.15 watts. So now that 140 lumens per watt turns into 140 / 4.15 watts = 34 lumens per watt. A plain ole incandescent bulb can do that.
So if someone got some credible info I would like to see it.
dereckbc,
If a manufacturer of LED products wanted to make their products inefficient then they would design using linear regulators. None I have looked at recently use linear regulators.
They use PWM current regulators.
One in particular that I have tested ran at 24Vdc and measured 0.45A RMS for an "appearant" input wattage of 10.8 watts. Each of 4 LEDs consumed approx 0.8 watts for a total "appearant" wattage of 3.2 watts.
If you look closer however the voltage waveform at the LEDS is PWM and thus the voltage across the actual LEDS is only present for about 1/3 of the time (on this unit tested). Thus the wattage that is consumed is much lower than the simple "appearant power" calculation leads you to believe.