Cutler-Hammer, and perhaps some other manufacturers, have a panel (BR) series where the left hand "ground-neutral" bar is bonded to the can by a 8-32 screw at the end of a "bond strip" that extends just short of the right hand bar.
If the panel is a service panel, the bond jumper can be installed using the same 8-32 screw.
With the bond jumper in place, you have a path thru the bond jumper to the "strip" held in place by the 8-32 screw into the panel enclosure.
I have found no indication that the left hand bar is "grounding" only and often grounded conductors are connected there.
It has long been a concern but apparently no violation.
With the addition of 200.2(B) to the '08 Code, do you see it as a violation to use the left bar for grounded connections ?