Voltage Drop and Power Factor
thomrk
When do you include power factor when calculating voltage drop for a branch circuit conductor? The voltage drop calculator that I use doesn't even have a place for power factor, so I was wondering if you assume the power factor to be 1.0 when just looking at the conductor itself.
I do and have not seen others consider power factor for branch circuit VDs. It may be worth while if you need to be very accurate for feeders, but again I usually don't. If using a calculator that does not account for PF you can introduce it using the I value: I(rms) = P(VA)*P.F. / V(rms) and then input that value into the calculator instead if I = VA / V value as often used in producing panel schedules.
Consider 3ph highly inductive loads. An example is starting an electric fire pump motor and keeping the vd to 15%. I tend to use table 9. Be sure to read the table notes.
This will require that you use math - not a plug-in-the-numbers calculator.
However, if all your branch circuits are 120V residential-like then I would likely ignore pf as already suggested
ice