2005 NEC Article 250.120 B

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Just to add to my post above. Article 250.120(B) is about EGC so I am not sure when that would terminate without a JB. There is more to this then so are seeing, I think. :)
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
I suppose so. Until its actually terminated or spliced, it serves no purpose.

So since it is not terminated I could leave only 1" of conductor in the box and be code compliant?

In reading the exception how would you explain a conductor terminating at an outlet. Use 100 definition for outlet.
 

Smart $

Esteemed Member
Location
Ohio
So since it is not terminated I could leave only 1" of conductor in the box and be code compliant?

In reading the exception how would you explain a conductor terminating at an outlet. Use 100 definition for outlet.
Less than 6" (or the 3" variation) is only a violation if you terminate or splice it. :D
 