Borrowing from another thread and following up on Dennis' comment,
would you pass or reject this ?
View attachment 5190
would you pass or reject this ?
View attachment 5190
I personally think it stinks, but after reading 480 Sparkys comments in that thread where the picture came from, that the 1 1/4" from the edge only applies to bored holes just had to read it for myself & have to agree w/ him.
300.4(D) Cables and Raceways Parallel to Framing Members and Furring Strips. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed parallel to framing members, such as joists, rafters, or studs, or is installed parallel to furring strips, the cable or raceway shall be installed and supported so that the nearest outside surface of the cable or raceway is not less than 32 mm (1? in.) from the nearest edge of the framing member or furring strips where nails or screws are likely to penetrate. Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by nails or screws by a steel plate, sleeve, or equivalent at least 1.6 mm ( in.) thick.
Read the correct section.
Read the correct section.
Quote:
300.4(D) Cables and Raceways Parallel to Framing Members and Furring Strips. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed parallel to framing members, such as joists, rafters, or studs, or is installed parallel to furring strips, the cable or raceway shall be installed and supported so that the nearest outside surface of the cable or raceway is not less than 32 mm (1? in.) from the nearest edge of the framing member or furring strips where nails or screws are likely to penetrate. Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by nails or screws by a steel plate, sleeve, or equivalent at least 1.6 mm ( in.) thick.
__________________
For years I have always wondered why we have to keep cables 1-1/4 inch from the edge of the stud, but yet if only a 2x4 stud, most device boxes have the cable entry closer than that from the back side of the wall.
I have never heard of an inspector picking on it as long as your cable fastening means keeps the cable 1-1/4 inch away, but if you are going to be real hard on enforcement this should not be allowed.
As shown in picture with cable running behind the box I've seen it fail and it should.
The reasoning behind the 1 1/4" is to prevent hitting the wireing with screws/nails when putting up drywall or other wall covering.
I have seen the wire running behind the box and it pass. I have also seen it fail just depends on the inspector that day.
I agree the design of the boxes will bring the wire closer to the edge than 1 1/4" so if an inspector really pushed 300.4 (D) he could require a nail plate behind the box. Oh, happy days
I think it looks like doo-doo, but I would pass it, not without giving the installer a hard time about it. The question I ask all of you that say "fail it" is why is that a "fail" but the NM into the top of the box "Pass" ? Both are the same distance from the stud face. What about the inside of the box at the back, it is within a 1/2" on the wall surface and plastic boxes don't stop nails to well?
I avoid this type of problem by placing my switches on a block to space them away from the door trim, not to get clearance for the NM but to clear the trim. The added distance from the "nailing face" is a plus. If I bring 1 or 2 NM's into a box, I use the hole that is farther from the stud face. When I need to go around a box (top to bottom) I go around the side.
Borrowing from another thread and following up on Dennis' comment,
would you pass or reject this ?
View attachment 5190
The pictures posted was just an example of the workmanship that is not there.
This was done all over the house.In a lot of cases I could not figure out why he went to the bottom of the box instead of using the available knock out on top.
After i got into changing & redoing a few I figured out he was pulling feeder wires to bottom.I guess this was his way of lableing the wires. And by the way our Inspector did ask that a lot of this mess be fixed.I called for a safety Inspection before I touched the work. The worst thing was the panels were set 18" to high.we lowered them to proper height.