I wonder if he meant amps instead of watts.
Uhhh...I'm an idiot. :roll: I did indeed mean
amps.
The spefics.
I retrofitted a bunch of bollard lights from 50W, 240V metal halide to 18W, 120V compact fluorescent and someone was insisting that I increased the load.
I have a side by side amp meter testing thing but it is only set up for 120V.
I connected the
18W lamp to the ampmeter and it drew
.36 amps.
I changed the tap on the
MH ballast to 120V, connected it to the ampmeter and it drew
8.2 amps.
I'll rephrase the question.
Does my retrofit (240V, 50W MH to 18W, 120V CFL) change the load significantly?
My logic says, .36A x 120V = 43.2W and .82A x 120V = 98.4W, therefore the watts and operating costs are substantially reduced. Am I missing something because I tested the MH @ 120V rather than the 240V they were originally operating at?
Pardon my ignorance but I am more adept at the mechanical end of this trade.