hurk27
 - Portage, Indiana NEC: 2008
Well I guess we could sum this thread up by saying, 2/0 SECs from a 200 amp meter to a double lugged 200 amp main in the first panel then 2/0 to the 200 amp main in a second panel is code compliant, as long as the calculated load is below the rating of the conductors.
230.90(A) exception 3 allows the installation
230.82(1) also allows the installation "other current-limiting devices."
which the 200 amp main in the second panel is "other current-limiting devices"
90.8(A) or (B) is vague and un enforceable.
Now we also for the most part agree most of us would not do an install like this, My own feelings would be not where these SEC's enter a dwelling, I don't see a problem outside no more then having unprotected SEC's outside, but in a dwelling where Joe home owner could add circuits I wouldn't, on industrial or commercial I see it all the time. very common on the back of a strip mall to see a trough with the riser pipe out the top, and maybe 3/0 into the trough with 4 or 5 100 amp meters dropped out of the bottom each tapped to the 3/0, calculated load never done yet they are still there.
So as in the Myth Busters own words, "This myth is busted"