dentist office design
quinn77
doing a design on my first ever healthcare facility. its a small dentist office that will contain 4 patient rooms with nitrous and oxygen, with a small storage room for both gases. art 517.60 tells me that the entire volume of each patient room up to 5 foot is class 1 div 1; however, ive seen these rooms roughed in as other than hazordous locations. am I misinterpreting this article?
517.60(A)(1) applies to hazardous (Flammable) anesthetics.
Nitrous Oxide is not a flammable anesthetic so you don't have a Class 1 location in a Dentists office.
Chris
Thanks Chris, that makes sense. I was thinking about nitrous in a race car...toooootally different.:grin:
Actually they are the same thing.
Nitrous Oxide is an oxidiser which means that it adds oxygen when added to a flammable liquid or gas.
Chris
Motorized Chair Wiring
If you have anything in the slab@ grade level in the patient care area's do not use pvc.
code ref please:cool:
517.13(A) Wiring Methods. All branch circuits serving patient care areas shall be provided with an effective ground-fault current path by installation in a metal raceway system, or a cable having a metallic armor or sheath assembly. The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding conductor in accordance with 250.118.