- EC - retired
Spent the last two days repairing old copper underground feeders. Direct bury. After the first find and repairs yesterday we turned things back on and still no power on one leg. I wasn't involved in the ditch work. "Didn't you check for other faults?" I calmly asked. "yea, but the tester didn't show any" Greenly tester that is good for 1 meg at 9 volts. They have a 1507 Fluke on the truck.
I went back this morning and found two more right away, including one that they thought was just a fluke yesterday. They had hand dug down the 4' to the wire but had missed the locate by a few inches to many.
After digging up and isolating another section the help told me his Greenlee indicated another fault and proceeds with another test which showed everything just fine. His face just dropped. I had him reverse the leads and of course the wire failed again. Megger proved it, .03 M at 34 volts.
When copper oxidizes does it always act somewhat as a diode or just when it has the rubber type insulation that was used in the past?