Riograndeelectric
- Lakewood Colorado
I received this email today form one of my customers ( Doctors office)facility was built in 2007. wired with MC cable. I have done a couple of service call here in the past to add a couple of Receptacle.
I am not sure but I believe all circuit are MWBC.any input in this would be help helpfull. I have to go out tomorrow and look at this problem
Thanks.
Cameron
Here is the power report that we ran on Friday. We recorded 4000 events in about an hour ( this is the max our monitor will record.) We do expect to see some activity when we run a power monitor like this, however this is really excessive. There are Neutral to Ground swells up to 7 volts, and voltage sags down to 105 volts. This many events in such a short amount of time can play havoc on the machines logic, and can damage several key components in the machine itself. From the looks of this I think that you might have a loose or poor ground on this circuit.
Please let me know when your electrician is done so that I can have my tech return and check the machine over for any other issues that might have been caused by this. Thanks,
Thanks.
Cameron