445.18(1)
Hendrix
New England
I haven't paid too much attention to this but it has me a little befuddled.
Does this mean that if the fuel has a shut off (which most generators do) that you would not need a service rated disconnect to kill the power :confused:
Read 445.18 (1) and (2) .So you still need a DICO.:)
A fuel shut off won't readily shut down a gasoline generator. It will run until the fuel on the engine side of the shut off runs out. In the case of a gasoline generator with carbs that have float bowls, they can run for several seconds or more after the fuel petcock is turned off.
I see readily shut down as having a kill switch or button for the ignition of the generator if it has one. (Diesels don't have ignitions so the fuel is shut off to stop the engine)
I am pretty sure the intent of the parallel notation was to apply the exception to generators that would be operating as the only available source of electricity. I just am not fond of the way it's worded.
The fuel valve does not qualify, as mentioned... but if the driving means (aka motor usually ;)) has a kill switch (i.e. on-off), that qualifies as "can be readily shut down".
What is "other source of voltage"?
Another would be a photovoltaic system...
So it doesn't matter what the source of the source is, only that it is a source that can energize the generator when the driving means has been shut down.
In a nut shell. If the gen. is the only source, withstanding the utility which would not be in parallel, and there was a remote E-stop then a disconnect would not be requried.