Can you use copper water pipe for a EGC if the pipe is bonded at the electrical service?
No ............................
Why don't you throw a reference like 250.118 out there with your posts?
I answered the question he asked, is that no longer the thing to do?![]()
Was this ever alowble ?
5-87- (250-50, Exception):
Secretary s Note: It was the action of the Correlating Committee
that this proposal be reported as "Reject" becaus~ less than two-thirds
of the members eligible to vote have voted in the affirmative.
It was the action of the Correlating Committee that further
consideration be given to the comments expressed in the voting.
This action will be considered by the Panel as a Public Comment.
SUBMITrER: Donald A. Ganiere, Ottawa, IL
RECOMMENDATION: Delete this exception.
SUBSTANTIATION: With increasing use of plastic plumbing repair
parts a water pipe that was effectively grounded -at the time it was used
as an equipment grounding conductor may be rendered useless by a
repair, of this water'pl]ipe. If the. repair is .made at a position on. the
pipe remote from the bonding connecuon the persnn making the
repair has no way of knowing that he has broken the equipment
grounding connection to a receptacle. Section 210-7 (d) exception
allows the use of GFCI type receptacles to replace ungrounded
receptacles. This installation of GFCI receptacles does not require an
equipment grounding conductor and would result in a safer
installation.Ihave submitted a companion proposal to delete 210-
7(c) FPN No. 2 which references the exception u) 250-50.
PANEL ACTION: Accept in Principle
250.130(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates
(4) For grounded systems, the grounded service conductor within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar within the service equipment enclosure
FPN: See 406.3(D) for the use of a ground-fault circuit-interrupting type of receptacle.
In some ocassion you may use the water pipe as an egc. Look at 250.130(C)
Must have beaten you by a milli-second.
Oh, it definitely was. Actually any conductive metallic water pipe system was acceptable as an EGC when one bonded anywhere along the cold water pipe until the early '90s.I don't recall that copper pipe was ever allowed as an EGC.
Dennis,
By what method do you locate your information ?
I know you are a good electrician, lots of experience, etc.,
and I am only asking what kind of pencil you use.![]()
Not that I have seen it, but this seems to indicate it may have been legal at one point, 93 or 96 reference:
You were allowed to bring a wire from the water line to an outlet if you were replacing a 2 wire outlet with a 3 wire. So, I guess indeed that in that very narrow sense, you could have used the water pipe as an EGC.
You are still allowed to do that. 250.130(C)