larrybartowski
I'm in MN. A customer of mine is being required by the local electrical inspector to add a grounding conductor to each of 4 elevators feeds. 2 of the elevators are being fed underground and 2 overhead, and all are with aluminum conductors. 2 Questions:
1. Does each elevator need its own ground per code? Or if its sized properly can they all be grounded from 1 ground conductor run back to the main service?
2. Can the grounding conductor be strapped to the outside of existing conduit or run in a separate conduit altogether?
Another more expensive option would be to remove the existing aluminum conductors and replace with copper to make room for the grounding conductor. Any advice is appreciated.