The SSGB grounding conductor should not be placed in ferrous metallic conduit. If local building
codes require metallic conduit or sleeves, the grounding electrode conductor shall be bonded to
each end of the conduit using a listed grounding bushing or a bonding jumper of the same size, or
coarser than, the required enclosed grounding electrode conductor (ANSI-J-STD-607-A-2002,
ANSI T1.334-2002, ANSI T1.313-2003 and NFPA 70-2005, Article 250.64(E)).